Hi everybody,
I want to use the EDM block of the SAFEX-C.12 for feedback loop monitoring.
Yet I am not able to Reset the Error of the EDM Block via external Rest.
The actual settings/wirings/interconnections are shown in the pictures attached.
Am I linking the external Reset correctly? Any thoughts were my mistake could be?
By the way, if i use the setting "als Block-Reset (Schließer) verwenden" in the Reset properties, I get Error F1333.
Thanks an regards 🙂
Solved! Go to Solution.
02-02-2023 05:45 AM
Hello MST,
I forwarded this question to another user ( @Dias ) who is more familar with that.
Your ctrlX SAFETY team
05-11-2023 11:10 AM
Hi @MST,
Unfortunatly in the current release the reset process of the EDM block is not well implemented.
As a workaround you can setup the Input Element Start/Reset as "Use as Alarm-Reset" and it will clear your EDM block. IMPORTANT: This will also, reset your logic. So validate if this workaround is useful to you.
If not, I would recommend to not use the EDM function block until the fix is done.
This topic is being tracked as Bug #584752, please look on the future release notes if this bug has been fixed or is still a known issue.
For further support, please contact Bosch Rexroth support team, more info at:https://docs.automation.boschrexroth.com/doc/893307806/service-and-support/latest/en/
Best Regards,
BRamos