When switching over from indradrive to ctrlX drive we face the following behavior.
The home switch is configured over the Ethercat Bus. Signal Control word.
But During Homing the axis is arguing that the reference input is not assigned. But its set on bit 15 as you see above
We now wired it to the drive. But this should be possible. What could be the cause ?
Solved! Go to Solution.
Please provide parameter set for existing, working IndraDrive solution and for not working ctrlX DRIVE solution. Use format "all parameters"!
See attachments for parameter files
Indraworks S-0-0400 is communicated trough signal control word (S-0-0145), homming is succeed
CtrlX doesn't reconize S-0-0400 trough the signal control word error C0607 pop up.
Previous Torque value was scoped on an older machine, this machines uses the index puls of the encoder for the reference run. This also generates a torque peak.
Added new parameter file of the X'axis machine with Indradrives, this machine uses the home switch (S-0-0400) within the control word.
Any news here or can this topic be closed?
we have now wired the home switch to the drive to reduce lag on this input. When communicating the home switch with EtherCat we have to consider the extra lag by the PLC cycle time (x ms)
This ticket can be closed.