08-09-2024 03:29 PM
we are working on a Projekt for controlling a robot with a CtrlX Core.
Unfortunately, there is a problem with the connection between the WebIQ and our OPC UA server, running on CtrlX Core. All certificates and licenses are instaled and active. The error shows in the WebIQ-Designer in the IO-Manager as "waiting_for_reconnect" (screenshot atached). We already checked the Port and IP for the communication. The Variables are currently shown, but while running the WebIQ-Projekt, they are not set in the CtrlX Core program. (WebIQ-Runtime and -Designer Version: 2.15.9)
Questions gladly
Many thanks in advance
With kind regards
08-09-2024 05:53 PM
A couple things to check...
08-12-2024 08:17 AM
Without providing a connect.log in trace mode this cannot be analyzed further, unfortunately. You can download the log in Runtime Manager. This usually shows you the errors and might indicate which of suggestions provided by @Sgilk might be the reason.
Can an admin please move this topic to the correct forum for WebIQ?
08-12-2024 10:09 AM
08-13-2024 02:58 PM
Hi Sgilk,
Thank you for answer. I overlooked the rejected certificates and select them as trusted. Now it works perfectly.
With kind reguards
08-16-2024 08:14 AM
Just as a quick note for everyone else reading this here: in most cases OPC UA servers require you to trust any OPC UA client certificate for security reasons. This is not an issue with WebIQ, but a security feature of OPC UA to prevent unconfirmed connections to the server - even using the correct credentials (like if they had been obtained somehow).
