FORUM CTRLX AUTOMATION
ctrlX World Partner Apps for ctrlX AUTOMATION
Dear Community User! We have started the migration process.
This community is now in READ ONLY mode.
Read more: Important
information on the platform change.
07-04-2022 09:10 PM
I am setting up a 4 axes demo with a XCD and a XMD. I did follow the document of Suitable Power ON/OFF ctrlX Drive and the parameters listed in the document are outdated for ctrlX WORKS WRK-V-0112.7. I figured out the parameters for XCD after having tried and errored. here is what I found for XCD.
however when I worked on the slave side(XMD) the manual shows using bit 0 of S240, but it doesn't work. I checked the parameters from the pull-down list and non of the similar ones worked. S240 showed 1 in the bit0.
I can get the XCD into AB through a power on/off switch, but not XMD. here is the error message I got when I switched the drive from PM to OM.
please advise the correct parameter for DC power control word on the slaves, or if I have missed some settings somewhere else. or tell me what is a correct way to switch the slave into AB using digital I/O to power on the slave drives.
Thanks,
Solved! Go to Solution.
07-06-2022 10:35 AM
On a XMD double axis drive you need to do that only for the first axis, not for the second.
07-06-2022 06:37 PM
I found out why the error message popped up when switching the slave drives from PM to OM. I had the S240 configured in the process data in ctrlX I/O engineering, which I had tested the power on by using PLC program.
when using digital I/O to turn the power the parameters for power handling can't be assigned in the process data. the bus communication overwrites the parameters in the slave drives.
that was good to have a chance to learn that. now all of the axes are up running. by the way the second axis of XMD double axis drive needs the S240 assigned to a digital input to be able to turn the axis from BB to AB.