Hello,
We have a actual problem in reading out the One Cable solution with the next example configuration:
WA-XD1-AXS-V-0204N-NN | XMD1-W1616ANA-01NETT0NNNN-S0204N2NNNN0NN | MS2N06-E0BHN-CMSK2-NNNNN-NN | CUD1-01ET-T0NNNN.
So the one Cable solution with encodertype CMS.
In this machine we have 9 ctrlX drives ( double and single inverters) with MSN2 motors ( CMS feedback) and 4 traditional Indradrives.
The traditional drives we installed for using FSoE and compatibility for our MAD motors.
We have checked/improved the Grounding in the E cabinet, and all cables are mounted correctly to the motor and ctrlX drives. ( so oke)
Cablelength: 15-20 meters per drive. Total cablelenght: 105 meter ( so oke)
The problem occures only when the drives are enabled. Motorspeed does not have a influence, one or more axis running neither. The error accures at random.
Only the ctrlX drives/ MS2N motors with the acurolink gives this F8022 error. Does somebody else have problems ( or not) with this combination?
Regards Johs Heijmink
Solved! Go to Solution.
03-29-2021 04:35 PM
Issue solved and further discussed in internal forum.
05-11-2024 05:03 PM
What was the solution for this issue?
05-13-2024 07:46 AM
The root cause for the error F8022 can be quite different:
- bad EMC, shielding or grounding conditions
- use of too long cables or too much cable connections in combination with drive parameter settings (e.g. PWM settings)
- use of wrong cable in combination with different drive firmware/runtime
Therefor please address to your responsible regional service or sales contact to sort out your particular problem if having a drive showing error F8022.