OPC UA connection issues
Eddie_Boman
Hi.
Im having trouble to get a working connection between OPC UA server and Web IQ.
I have done steps accordingly to these 2 videos
https://www.youtube.com/watch?v=12v1haa9OSU
https://www.youtube.com/watch?v=JPHyx5xX3-8
I had to modify this:
The problem comes below:
Connection established but rejected by OPC UA as you see.
When the first one comes up i click trusted.
Then after a while a second comes up and if i click trusted the following window appears.
If i look in WebIQ manager while this happens it says connecting and the light is yellow.
I never get the connected status and a green light.
webiq-sk
Frequent Contributor
Can you please verify that the time is setup correctly on the system?
Please also note that the error message in red comes from the OPC-UA server, not from WebIQ.
That helped.
The date and time was incorrect.
Thank you for your help.
HmiGuide
Hint: It's better to use 127.0.0.1 (=localhost) when your WebIQ server runs on the ctrlX. Then the project it's working on each ctrlX.
opc.tcp://127.0.0.1:4840