01-20-2023 11:19 AM
Hi.
01-25-2023 09:24 AM
Could you please confirm that you are using:
Could it be that there is a doubled input address range of the ctrlX IOs on the EtherCat and the Camera on Ethernet/IP? As each of the communication line has its own setting and does not necessarily know what the other side is set to.
01-25-2023 12:21 PM
To clarify the ctrlX IO is connected directly in-line to the CORE X3+, with EtherNet/IP via port (XF51/eth1).
The issue has been resolved, there is a bug with version 4.4.0.0 of the Ethernet/IP Scanner, downgrading to 4.3.0.0 allows the ctrlX IO to function normally while the Ethernet/IP device is running.
01-31-2023 01:58 PM
I have got the same problem as you. I have got ctrlX Core X3 connected via XF50 to ctrlX BusCoupler with DI16 and DO16. I have also got the Ethernet/IP Scanner (Version 4.4.0.0) with EFC5610 with MultiEthernet Card connected via XF51.
The Ethernet/IP is working, I can control the EFC via PLC App.
The IO's are not working. I can set the output via PLC App but nothing happens. The output is still FALSE. I also checked the DataLayer - it is working, I can set an output to TRUE and there is 24V and the LED is present. So there are some problems with setting the outputs via PLC App.
We can't find 4.3.0.0 version in the Collaboration Room. The 4.4.0.0 version is now also unavailable, it isn't there. We downloaded it on 27.01, then is was there...
01-31-2023 02:48 PM - edited 01-31-2023 02:49 PM
@Filip_K We removed the version 4.4.0.0 because of some problems that were found. 4.3.0.0 was not evaluated by Rexroth R&D and so is not available in the collaboration room. if you need a later version then 4.2.0.0 please get in contact with CodeSys directly. Is there a reason for you to use a later version?