FORUM CTRLX AUTOMATION
ctrlX World Partner Apps for ctrlX AUTOMATION
4 weeks ago
Hello,
I'm trying to make a simple project in ctrlX Safety Engineering, and when I'm trying to connect to the ctrlX Safety the following warning appears: Current document configuration is not synced with configuration of
connected device. The layout diagnosis is not possible.
And then it won't let me do anything, I can only disconnect.
Does anyone knows how to solve this?
I'm using SAFEX-C.12 and ctrlX SAFETY Engineering 1.8.3.10207.
Solved! Go to Solution.
4 weeks ago
Hello @AndreR5 ,
The message is "normal" when the opened project that just connected does not match the project currently running\loaded in the control.
Please try clicking on the "Secure" (key) icon then enter default password (boschrexroth). If successful, the "Send Configuration" and other icons should become active then you can Send Configuration (download) the project.
HTH
4 weeks ago - last edited 4 weeks ago
Thanks a lot! Now it's working properly.
Can you provide me a link where you screenshot this step?
3 weeks ago
Hello @AndreR5,
Glad to hear it is working. Currently the clip is part of the ctrlX SAFETY Workshop material. Attached is the document. It is in process of being added to the How-To section of the developer community.
3 weeks ago
@ctrlXProgrammatoreThank you!