FORUM CTRLX AUTOMATION
ctrlX World Partner Apps for ctrlX AUTOMATION
Dear Community User! We have started the migration process.
This community is now in READ ONLY mode.
Read more: Important
information on the platform change.
05-30-2023 08:57 AM
Hi all,
if i like to scan device after ethercat master, the tool says no slave found.
I use an CtrlX COREX-M-X3-11 with integrated Ethercat extension and i also plug the powersupply and i can not find any devices. Also if a configurated by my one the bus and load to the device it is not working and i have and topology missmatch. Is there any problems with the hardware version cx_m4p_a? I connect also the extension from the ethercatmaster port to the extension EC in port.
Solved! Go to Solution.
05-30-2023 09:10 AM
Hi,
did you activate the EtherCAT master on the ctrlX CORE first, before you tried the scan?
See the section "Configuring the EtherCAT master" in the manual.
05-30-2023 09:23 AM
yes of course, i see also the topologie is not ok. If i opening the ethercatmaster i see my configuration and the hint that they not connected
05-30-2023 01:18 PM
Hi Zimmbo,
not sure if I got you right.
But the Ethercat on a ctrlX CORE Plus is wired internally, you are not allowed to connect the XF50 to any other port on your device.
Most likely this will cause some loop.
Maybe you can make a picture of your setup?
Which versions of apps and Works are you using?
Regard.
05-31-2023 07:28 AM
Hey all,
yes i make a loop if i connect ethercat master twice. Maybe their can be a hint, that it not necessarry to connect the XF50 (EthercatMaster) with the XF23 from the internal extension. Also if their build a loop, maybe a error message will be helpfully.