My ethercad master do not go to OP-state because the device _9251_ethercad_Drive and device _9251_ethercad_brake do not can go to Safe-OP.
(this due to the option: Slave have to reach the master state. ) if this option is off then the master go to OP. but my slave device _9251_ethercad_Drive and device _9251_ethercad_brake still stand in PRE-OP.
At the diagnostics of the master i see the follow message:
As PDO: the follow content is assignt:
at the attachement the XML file from the supplier of the device.
regards,
Solved! Go to Solution.
08-14-2023 01:38 PM
Hello,
I had a similar issue when I had turned on the AoE option (under expert settings). It may be worth a try to disable this.
08-18-2023 09:47 AM
Hi,
I try to test the Master enable, but without succes.
08-18-2023 09:54 AM
in addition i have recieved the following answer for the question from my supplier:
08-18-2023 01:19 PM - edited 08-18-2023 01:36 PM
As our engineering tool is using the data provided by the .XML file and we do not have any hardware to test, its quite hard to say what should be wrong here.
To be sure we are talking about "burster 9251 Fieldbus Controller" module right (external supplier page).
Did you ask the supplier if the data used is correct:
Could you give me the contact of the supplier so we can have a direct talk about that? Feel free to send me a private message.
Please also send us the IO project used and describe your application.
08-18-2023 02:34 PM
08-18-2023 03:46 PM
We will check this.
Could you please:
08-18-2023 04:20 PM
08-22-2023 08:52 AM
Could you please switch on the traces of the Ethercat master via the data layer (trace/rexroth-automationcore/units/comm/ethercat), create the problem and export the logbook again?
08-22-2023 09:47 AM
08-24-2023 08:10 AM - edited 08-29-2023 06:31 AM
Thanks to your information we could figure out whats the matter:
Like the error says and also the device supplier says targets 0x1C12 and probably also 0x1C13 are written but read only.
There is a setting in the "Expert Process Data" in our ctrlX IO Engineering that tells the master to do so:
In fact these settings are predefined as active in the device description file provided by you. So it seems to be a predefinition fault in the ESI file. Could you please get in contact with you supplier to clarify this?
As workaround as long as there is no correct file:
08-24-2023 11:42 AM
Dear,
When deselect the "PDO Assignment" and select "PDO Configuration" i still get the errot message:
When select the "PDO Assignment" and deselect "PDO Configuration" i still get the errot message:
When deselect the "PDO Assignment" and deselect "PDO Configuration" i still get the errot message:
08-29-2023 07:56 AM
Just to be sure, after changing the setting you did another download of the EtherCat configuration and tried to switch up again? I will get in contact with our R&D.
08-29-2023 09:01 AM
With assignment and with configuration on, then download, and powercycle this is the result:
Without assignment and with configuration on, then download, and powercycle this is the result:
Without assignment and without configuration on, then download, and powercycle this is the result:
With assignment and without configuration on, then download, and powercycle this is the result:
08-29-2023 09:42 AM - edited 08-29-2023 11:39 AM
Thanks again for the clarification I had another talk to our R&D and we see that ESI file seems not to fit to your device connected to the EtherCat master.
UPDATE: Supplier sent a new device descrption file that should be tested. @Henderickx waiting for your feedback.
08-29-2023 12:40 PM
Dear,
The reaction of Burster: "The main problem is, that the Bosch PLC does not support the online reading of the device configuration and the Bosch PLC does not support to load a TwinCAT configuration file."
I recieved the new XML file from them but still without succes.
I sent then the follow screen shots from the errors depending on the state of : "Slave has to reach master state "
08-29-2023 12:43 PM
Could you please add the new device description file?
08-29-2023 01:00 PM
11-03-2023 11:58 AM
This topic has been resolved by creating the fitting XML file on customer side directly.