When trying to do a frequency analysis using ctrlX compact drive in combination with an MSK motor I get the message "Excitation Amplitude needs to be configured", and the detailed view on the Oscilloscope is empty for all the tests.
I find no documentation on how to set the excitation amplitude nor a description of what it is or how it works.
Please could I have some advice on this topic? The tests have always worked fine on Indradrive with 2nd gen control.
Solved! Go to Solution.
06-04-2024 09:16 AM
Could you please add a parameter export of all parameter to this post, so we can get some more information which devices and settings are used?
06-05-2024 02:26 PM
06-05-2024 05:19 PM
Normally the sequence is like shown in here and works exactly the same with ctrlX DRIVE as with IndraDrive
1. Activate "Easy Startup mode"
2. Press the Icon and you will get a suggestion value for the excitation (like in here the value 235,3729)
3. Take over this excitation value by pressing the icon
4. Enable the drive
5. Carry out the frequency response analysis
6. Evaluate the frequency response analysis
06-06-2024 09:23 AM
Hello Uwe,
Correct this is the method I follow, all the below points are green and the test runs as expected
However the display results is always empty (no reading/graph). This is true for all six possible tests. I am running the tests after having done an autotune, and accepting the reccommended parameters.
06-06-2024 02:14 PM
Which Drive Engineering Version are you using?
06-06-2024 02:40 PM
Hello Gunnar,
This is the version I have
06-07-2024 07:48 AM
There is a 1.28.1 ctrlX DRIVE Engineering available in the collaboration room. Try this version.
Another hint is to close the oscilloscope and then start the frequency analysis. The oscilloscope will be opened at the end of the measurement.
06-10-2024 12:36 PM
I have re-tested with 1.28.1.
The result is the same, all steps run perfectly including measurment. But my display results remain empty.
After Autotune procedure, all of the tests are empty. Before the autotune, I get a graph for Current loop analysis, and for Analysis of speed loop, but all the other measurements are empty as well.
06-10-2024 12:37 PM
For more information, this is on my Windows 10 laptop. I found the same results on a customer's Windows 10 IPC.
06-24-2024 01:55 PM
Reason for the reported behaviour of "Empty frequency analysis" is the slow communication from PC over the ctrlX CORE to DRIVE.
If using a direct USB connection over the pannel erverything is working fine.
Another solotion for this issue is to activate the EoE communication from the ctrlX CORE to the DRIVE. Please follow the instructions given in the HowTo