CtrlX Core X2 Network Drop
CQ2023
Hi, I am using CtrlX Core X2 to connect IO module, when the network cable is disconnected from X2, the data transfer in PLC project is still working, why no alarm occurs in the system?
Just to make things clear, you connected some IO modules to the EtherCat slot XF50. Your communication and data exchange is working. Then you unplug the ethernet cable from XF50 and no warning/error is coming up?
Could you please tell us the version of the apps on your ctrlX CORE or send us a system report?
Yes, your description is exactly correct, so I need to know if the X2 does not perform network status diagnostics after successful communication with the slave?
My Core UI Version is V1.18.
I am attaching the system report below, thanks.
In your diagnostic logbook export I can see many errors that PLC detects a missing link to the IO slaves.
In my ctrlX CORE X3 I can see reactions of the EtherCat master status and also on the "Home" page:
ctrlX CORE web UI EthgerCat master status disconnectedctrlX CORE web UI EthgerCat master status disconnected
Is this not happening at your side? Which error would you expect?
Seeing EtherCat diagnostic in ctrlX CORE logbook is not implemented right now.
Actually, when I unplug the network cable from  X2, I can see the ethercat information in core UI:
 no errors occur,  and the status of ACS2 in PLC Engineering DataLater_Runtime is OK, too.
later, I replug the network cable, it show in X2 Core UI like this:
So I have no way to prevent the CORE network cable from dropping.
the diagnostic log is attached as below.