FORUM CTRLX AUTOMATION
ctrlX World Partner Apps for ctrlX AUTOMATION
Dear Community User! We are updating our platform to a new
system.
Read more: Important
information on the platform change.
05-23-2024 08:28 AM
I have a single channel output design which uses SIL3 Qx8_PP to drive a Hydraulic Valve with no feedback.
If the Hydraulic valve is a well tried component with High MTTFd, is it possible for this to be a PLc circuit? Or is this specifically excluded by the manual?
In the SAFEX installation manual Section 13.3.4.2.1 Single-channel switching relay or semiconductor output without testing it states that only PLb is achievable.
In Table 90 there is mention of SIL2 outputs with Category B circuit. However, there is no mention of SIL3 Outputs with Category 1 circuits. Is this a deliberate exclusion or is this perhaps something that was not thought of?
https://www.boschrexroth.com/media/a3953377-1914-4249-94e7-a6dfa2df9292
Solved! Go to Solution.
09-18-2024 11:01 AM
Hello Bruce,
attached please find a Sistema Performance-Level calculation, as I would do it for your application.In my opinion the examples, meant with good intentions, in the Safex-C manual are sometimes a bit misleading.
In my opinion it is completely fine to use the 2A output without testing and a well tried valve with the result of PL=c.