04-04-2023 02:18 PM
Hello
I’m trying to setup an FSOE connection between two SAFEX-C.12 cpu-s. I managed to setup one cpu to be the master on the network. The cpu status is RunIntern with permanently illuminated yellow light. That cpu is waiting for slave device connection.
I tried to setup the slave device, but I don’t find any parameter or option to do that. I found WEBINAR snippet about this topic (link down below). Where the connection is established between two SAFEX-C.15 cpu. But I found difference in SAFEX-C.12 and SAFEX-C.15 parameters.
It looks like in SAFEX-C.12 cpu I can't set any paramter to be an FSOE slave. I'm looking for any help to find where find such a parameter.
I attached my project files if its helps to troubleshoot my problem.
Thanks a lot.
Csaba
Webinar Link: https://developer.community.boschrexroth.com/t5/ctrlX-SAFETY/SAFEX-and-IndraDrive-FSoE/m-p/70879/thr...
04-11-2023 09:17 PM - edited 04-11-2023 09:33 PM
Hello @CsTemesvari ,
sorry that no one answered over Easter holidays.
In fact I cannot see anything wrong in your Master and Slave configuration.
Did you connect the connection between FSoE-Master (SAFEX-C.12 #1) and FSoE-Slave (SAFEX-C.12 #2) via a Copy action on the EtherCAT-Master (see e.g. https://developer.community.boschrexroth.com/t5/ctrlX-SAFETY/SAFEX-and-IndraDrive-FSoE/m-p/71369#M17...)?
The Controller is indicating a non-established FSoE-Connection by these two things, that you are reporting:
Additional findings:
No findings but just indication:
@Dias : Can you please check and give additional hints, if necessary.
@CsTemesvari : Please mark as solution, if this helped.
Best regards
Your ctrlX SAFETY team
04-19-2023 11:03 AM
Hello @AllAutomation
I have tried everiting you suggested in you reply (connection adress change, not using Fast channel). But unfortunetly nothing helped. The sympthoms are the same.
MASETER: RUNINTERN (yellow LED permanently light up)
SLAVE: RUN (green LED)
On both controllers the configuration is locked.
The EtherCar communication is running on a Rexroth VPB40.3 IPC using twincat. The ethercat diagnostic shows everithing is OP state.
I try to get my hands on at least one SAFEX-C.15 controller to try the communication but unfortunetly no success.
Thanks for any further help!
CsTemesvari
04-19-2023 12:41 PM - edited 04-19-2023 01:30 PM
The only possibility I see is that you did not close the FSoE-Connection on your EtherCAT-Master:
Did you connect the connection between FSoE-Master (SAFEX-C.12 #1) and FSoE-Slave (SAFEX-C.12 #2) via a Copy action on the EtherCAT-Master (see e.g. https://developer.community.boschrexroth.com/t5/ctrlX-SAFETY/SAFEX-and-IndraDrive-FSoE/m-p/71369#M17...) or the appropriate configuration of the EtherCAT-Master function where you link the two SAFEX-C.12?
Did you import the correct ESI-Files to TwinCAT that are fitting to the FW Version or your SAFEX-C.12 devices? This should not make a problem, since the ESI did not change since March 2021. The only relevance is the Modules.xml used starting from 1.0.1.19 to cover the SMMC-over-EAP/EtherCAT. Hmm ...?
@Dias : Please have a look and give assistance to the user! Thank you.
@CsTemesvari : Please contact @Dias , if he does not answer to this request. This communication between two SAFEX-C.1x is his favourite example for FSoE cross communication.
Best regards
ctrlX SAFETY team
04-19-2023 01:17 PM
Somehow I totally missed this part of the Webinar. I will try it, and get back to you with the resoults.
Thanks fort the really fast reply.
Best regards
CsTemesvari
04-19-2023 01:45 PM
as you said you are using a TwinCAT FSoE-Master. In this case you find the description to setup an FSoE-Connection in the Installation Manual:
HTH
Best regards
ctrlX SAFETY team
04-20-2023 01:39 PM
Thanks for any help you gave me in a past few days.
04-20-2023 07:01 PM
Your very much welcome! 😅 Finally we made it.