Dear all,
I try to create a ladder diagram for a three filling tank using CtrlX PLC version 1.20.7 and CtrlX Works 1.20.11 into a VirtualPLC. I compile the program (Generate code F11), download it, login (Alt+F8), and start (F5). How ever, I did not see status of the coils (on/off) and I can not modify state of a contact. See image in the attachment.
Please help. Thank you very much in advance for your help and attention.
Warmest Regards,
Suryadi
Solved! Go to Solution.
2 weeks ago
On the screenshot it looks like your LD program is not called anywhere, as it is grayed out. It needs to be called directly from the task manager (see 2Task Configuration") or another program already called by it.
2 weeks ago
Dear CodeShepherd,
I replace PLC_PRG (default) with TankFillingDeviceSolution_LD.
It works now. Thank you very much for your help.
Warmest Regards,
Suryadi