03-09-2023 10:46 AM - edited 03-09-2023 10:49 AM
Simple question as topic.
S20-ETH-BK will connect with one digital and one analog input modules, like S20-AI-4-I and S20-DI-16/4.
03-15-2023 01:44 PM
here you find the information about connecting S20-ETH-BK with IoT Gateway Software:
03-16-2023 01:55 AM
Thank you for the answer.
Since we got S20 module leading time issue cause of semiconductor problem, we want to change IO modules from S20 to CtrlX.
Therefore I have another question:
Can I use PR21 with IIOT software to read signals from CtrlX bus coupler XB-EC-12?
03-16-2023 09:00 AM
This is not possible. The S-20 Bus coupler driver within IoT Gateway software is based on Modbus. The ctrlX IO bus coupler is available with EtherCAT as protocol only.
03-16-2023 09:27 AM
OK, thanks, then we will go with CtrlX solution.
But we still have some S20 IO station with S20-ETH-BK bus coupler in stock, if I want to use CtrlX core to read signal from these S20 IO station, I need Modbus TCP License installed in CtrlX Core, am I correct?