Hello ,
I change the Process Data Telegramm of an IndraDrive Cs in ctrlX Engineering :
Afterwards I do "Transfer field bus configuration " .
EtherCat and IndraDrive Cs go to OP without any errors .
When I have a look in the data layerafter refreshing I only see one parameter : at the inputs the DriveStatusWord and at the outputs the DriveControlWord .
On the ctrlX core are versions 1.14
The ctrlX IO Engineering is version 1.16
What can be wrong ?
Thank you .
Solved! Go to Solution.
ctrlX IO Engineering 1.16 is not generally compatible with the EtherCat runtime app 1.14. Could you please have a try with corresponding versions?
Further more please add names to the variables, as the names are used to create data layer nodes.
Any news here?