FORUM CTRLX AUTOMATION
ctrlX World Partner Apps for ctrlX AUTOMATION
Dear Community User! We are updating our platform to a new
system.
Read more: Important
information on the platform change.
06-05-2023 02:06 PM
just a clarification regarding XAS4 accessory for multi line arrangement: my configuration is like this:
Based on the documentation I would need qty 1 XAS4-WM-U005-NN at XLC side and qty 1 XAS4-WL-U005-NN at XVR side, correct?
Then because of the XVR 72 kW I would use 70 mm^2 cable cross section.
70 mm^2 cross section seems to fit just in the XAS4-WL-U005-NN accessory but not XAS4-WM-U005-NN, how to deal with this situation?
Solved! Go to Solution.
06-12-2023 04:11 PM
I would recoomend to place the XMS 150A connected over the XAS4 and have the XLCs at the end of the line, like
XMS 150 - XMS 30 - XMD 1616 - XLC - XLC.
The you can use 2x XAS4-WL-U005-NN