Hello,
our customer would like to configure the cyclic data for Profinet. Unfortunately, only 24 bytes are possible. Is the data width really limited to 24 bytes? Shouldn't it be 24 words?
Solved! Go to Solution.
05-13-2022 02:29 PM
Sorry, in the very moment there is a bug present which limits the number of cyclic data to:
- 9 data elements (parameters) in total
- 9 x 4 byte = 36 bytes in total
But the correct foreseen number is:
- 15 data elements(parameters) in total
- 15 x 4 byte = 60 bytes in total
The bug will be fixed in the next relesae of firmware/runtime AXS-V03