Hello,
I have a question regarding about the new DA IO expansion functionality in the CtrlX plus drive. I sa that that option give the possibility connect to the drive 3 analog input, but will this analog inputs parameters readable and available on the Codesys PLC as an Input ? Will the correspoding parameters available and configurable in the drive EtherCat drive interface with the Ctrlx core ??
Many Thanks
Giuseppe
Solved! Go to Solution.
05-03-2022 10:00 AM
The analog input actual values can be of course read in the correlating parameters P-0-0229, P-0-0208, P-0-0228. See attachments.
If provided over the cyclic interface they can be read as well in real time from ctrlX CORE or if not provided cyclically over single parameter access.
Similar as well the target parameters, the anlog input is mapped to, can be read.