FORUM CTRLX AUTOMATION
ctrlX World Partner Apps for ctrlX AUTOMATION
Dear Community User! We have started the migration process.
This community is now in READ ONLY mode.
Read more: Important
information on the platform change.
4 weeks ago
Hello All,
I want to do a FRF manually in the drive by generating the noise from drive integrated signal generator and During this process I want to capture the data for 100s with 0.25ms time period but the drive oscilloscope in the drive won't allow me to take this mesasurement, Please refer to the image below,
Could you please help me how I can perform this test? if its not possible from the drive could you please help me with other solutions?
Thank you
Solved! Go to Solution.
4 weeks ago
This is simply not possible. Maximum are the mentioned 4096 points. Only way would be to use the control system exchanging the requested signals over the cyclic communication and then use methods on the control to get access to the signals.
4 weeks ago
Hello Uwe,
Thank you for your reply here as well. I should have updated this post with the reply I got from you with direct contact.
For customer the EtherCAT is slow as they want the trace points every 0.25ms.
3 weeks ago
Mind that one can run EtherCAT on a 0,25 ms cycle. Of course the control has to support that.