Hello everyone,
i tried to use the DeviceTrace object inside of an PLC project, but unfortunately the online list does not show any entry...
I did it like described in the manual R911403763 on page 248/249:
What do i have to do to trace the CPU load via PLC Engineering?
Thanks in advanced!
Solved! Go to Solution.
Hi Maurus,
the description refered needs to be updated since the mentioned Trace functionality is focused on PLC symbol-vars. ctrlX parameters are not supported right now.
Docu gets updated. Use Trace exclusively with symbols.
Update regarding access of ctrlX parameters (core-load, task-timing needs) will follow.
Bye Jens