FORUM CTRLX AUTOMATION
ctrlX World Partner Apps for ctrlX AUTOMATION
Dear Community User! We have started the migration process.
This community is now in READ ONLY mode.
Read more: Important
information on the platform change.
03-26-2024 09:14 AM
The customer is connecting PR21's power cable directly to the production line's power source, which is daily powered On in the morning, and powered Off in the evening. Due to this daily sudden power Off, PR21 is not performing well after being powered On next day (not able to to ping or communicate). PR21 can work well after being restarted. Howerver, the customer don't want to manually restart PR21 everyday.
Is there any document mentioning clearly that PR21 should not be suddenly powered off like this?
Thank you very much.
04-08-2024 01:09 PM
Hello,
i dont find any hint that you must use a UPS. have a look at the screenshot of the documentation:
Peter
04-09-2024 04:32 AM
Hi Peter, thank you for your reply. There are about 50 devices PR21 installed in customer factory (not Bosch plant). These PR21 are connected to production line's power source properly as your diagram. However, everyday, the production line is powered On at 8:00AM and is powered Off at 6:00 PM. Hence, PR21 is powered Off without being shutdown properly by its own power switch. Some devices (PR21) works well next start, some device doesn't. The customer asked me to fix those PR21 which is not working on next start. I want to show to the customer that they are treating the device in improper way (power off the power source of the production line, without shuttingdown the PR21 properly). However, the customer says that there is no documents/user manual mentioning that.