Different sensors have different output curves for 4-20 mA.
Where and how can I map the curve to the analogue values and convert 4-20 mA to lets say 0 - 100%?
Solved! Go to Solution.
02-23-2023 02:24 PM - edited 02-24-2023 07:57 AM
For the standard ctrlX IO analog input modules you will have to make this mapping inside of your application, as they do not know anything about the voltage/current source.
We are working on temperature modules that would fit to your application.
EDIT: @jacaré Prototype versions are planned for end of April 2023.