Hi colleagues,
I'm trying to set up Fixed stop function on a XCS 23A with FWA 0402.02. Unfortunately, whenever the drive switches to OM the following diagnostic message is thrown:
C0242 Multiple configuration of a parameter -> S-0-0423
Looking at S-0-0423, it complains about S-0-0149 being duplicated at S-0-0027.
I expect this to be possible, since it takes two bits to set the function, according to the documentation.
How can I setup fixed stop through signal control word?
I'm attaching the parameters file with All Parameters enabled.
Solved! Go to Solution.
01-24-2024 07:06 AM
Hello
in the signal control word commands can be executed with only one bit.
please erase bit 13 of the signal control word and start the command with bit 12