Hello,
I try to use variables from plc node in datalayer (attached picture) but the sym folder destinated for variables is empty. I tried with two different configurations, CtrlX drive Core and CtrlX Core virtual. From plc app all looks fine, no warning on Datalayer. Can you suggest me a hint on this topic?
Thank you!
Solved! Go to Solution.
01-16-2024 11:38 AM
Hi @Catalin
did you add the gvl also into the Symbol Configuration?
See this detailed how to: Set up a ctrlX PLC project to publish variables to the ctrlX Data Layer. Please check if you configured every step (especially step 7).
Best regards,
Nick
01-16-2024 12:14 PM
Hi,
I forgot to check it. This was the reason.
Thanks a lot!