C# data type problem with EAL IParameter.WriteData Method IndraDrive
LeoB
I have a problem with the IParameter.WriteData Method using C# on CtrlX Core.
I want to set an IDN in "P-0-0023" via the IParameter.WriteData Method in C# on the CtrlX Core.
Docu of method only contains an example on how to write an int:
https://apps.boschrexroth.com/docs/oci/eal/?topic=html/a75857a0-f90e-1bed-e5c0-c31531886d3d.htm
Docu of IndraDrive PSB Parameters:
https://www.boschrexroth.com/documents/12605/25199817/R911328651_14.pdf/5ad2c515-c201-9666-83ac-6c5d...
So as a first step i printed all possible IDNs using "S-0-0025" using the following code:
 And i got the following print in the console:
So as a next step i tried the following code to set an IDN in "P-0-0023".
But both tries didnt work out 😞
Does anyone know how...
1) i can print all the IDNs from "S-0-0025" in a readable way?
2) how to set an IDN in "P-0-0023"?
Thanks a lot!
Leo
Could you give us some more insights in your setup?
  • Your IndraDrive is connected to a ctrlX CORE via Ethercat and EoE is active?
  • You are suing the EAL library to talk to the drive
  • Where is the EAL running? is it on your PC or did you pack it in a snap?
Thanks for your reply 🙂
    -- Yes, IndraDrive is connected to a CtrlX Core via Ethernet. The communication is working well.
  • You are using the EAL library to talk to the drive?
    -- Exactly. In detail, i want to use the drives Oscilloscope function to read data. To activate it, a few parameters must be set before reading the data. The IParameter.WriteData() Method works fine when it comes to setting integer values, like for P-0-0020. I used the Method multiple times and it worked. The only problem is: I don't know how to use the Method to set an IDN (for example for P-0-0023). Which data format must be used?
    -- The C# program is packed in a snap and running on the CtrlX Core.
    Summary:
    The whole setup is working well. Using IParameter.WriteData and IParameter.ReadData are working well with binary or decimal variables. The only thing I can't do is to use the IParameter.WriteData Method() to set an IDN, for example for P-0-0023. The documentation says, the input is of type "IDN" with a length of "4Byte". How does a format of 'IDN' looks like in C#? Here are the documentations:
    Bildschirmfoto 2021-12-08 um 16.13.43.pngBildschirmfoto 2021-12-08 um 16.11.11.png
    Thanks a lot for your help!
RexCode
Hello LeoB
please try to write the value of P-0-0023 by type of System.UInt32 (4byte).
You can calculate the parameter type (IDN) by an offset. For S Parameter the offset is 0, for P Parameter the offset is 32768.
Example:
  • S-0-0051 = 51
  • P-0-0048 = 48 + 32768
Christoph