02-08-2022 08:53 PM
Online change fails with the following error. After this download is required.
02-09-2022 08:50 AM
Performing an online change is only possible, when no IEC task is running currently. The system tries up to 10seconds to detect a time gap to activate the online change. From my point of view it seems that the system load is nearly 100% on core2. You can test this, if you set your apllication to stop and do the online change. But it is recommended to reduce the load on core 2.
02-09-2022 09:51 PM
02-16-2022 04:36 PM
I continue to see this hourly. Is there a better way to get the data required to show that this is happening?I have to restart my machine at least once an hour while developing.
02-17-2022 12:43 AM
Here is another data point. I started stopping the controller to do online changes to see if it was related to the processor being overloaded. It still occurs. Are you saying this is a problem with the motion kernel? I only have 4 axes and a kinematic configured.
02-17-2022 06:43 AM - edited 02-17-2022 02:08 PM
to see the cpu load in a better way please go to
Settings/information - tab performance
Update:
at this screen we see only the NRT-Cores and not the RT-Cores. And the PLC is running at an RT-Core -> so no big info regarding this problem. Sorry for this.
Only for confirmation can you please check the taskmonitor at the PLC engineering.
03-03-2022 09:24 PM
Here is a plot of the cores
and here is the fault I received this last time. This continues to happen every 15-20 online changes
03-07-2022 03:10 PM
Any other items I can provide to help understand and resolve this?
03-08-2022 02:54 PM
Hi Alex
no idea why you get this message. The core performance seems to be quite ok.
I'm afraid I have to try to reproduce this issue at my side. Please can you provide me an archive of your project + a save of your app-data. Depending on the size you can sent it per email / ad hoc...
jochen.mueller@boschrexroth.de
Jochen
05-18-2022 10:21 AM