With PLC variables it is possible to add a comment and include this comment in the symbol configuration.
How can we now display this comment in the datalayer? (core and app versions of RM21.07)
Thank you in advance.
Solved! Go to Solution.
11-18-2021 12:55 PM
At the moment there is no possibility to get this information to the Data Layer. I will talk to our R&D if and how we could implement this.
05-13-2022 05:33 PM - edited 05-13-2022 05:35 PM
This feature was implemented in the PLC runtime app version 1.12.
Please make sure you have following settings:
PLC symbol configuration comment settings.png
Then you will find the comments in the Data Layer: